    I have only been using the 350 volt 12 volt Ray WU power supplies but I just plugged in 2 of the 4 supplies and they keep blowing the house fuses, so they are obviously faulty. I have been reading that Meanwell seem to be a better quality supply even though they are more expensive. I have been on their website and I'm a bit confused about all the different types that they have. Can someone recommend which ones I should get and is there an Australian supplier that you recommend?
     
  2. David_AVD

    David_AVD Good news, everyone!

    Joined:
    Jun 12, 2010
    Messages:
    3,345
    Likes Received:
    22
    Location:
    Victoria Point (Brisbane)
    I sell the Mean Well SP-320-12 power supplies.
     
  3. plasmadrive

    plasmadrive Full Time Elf

    Joined:
    Jan 12, 2012
    Messages:
    205
    Likes Received:
    5
    Location:
    Elk Grove, CA
    I am sure you meant 350 watt not 350 volt... right?
    Actually, look at the specs, they have one hell of an inrush current. They may not be defective at all.
     
  4. rvenegas

    rvenegas Apprentice Elf

    Joined:
    Apr 9, 2013
    Messages:
    60
    Likes Received:
    0
    Location:
    Valencia
    Find Me On:
    I have 3 of those and i tested them the first day the arrived. First test was to keep them turned on for 24 hours with no load. Second test was to test them 30 minutes with 50% load and finally third test was 80% capacity (230 watts) for 15 minutes. It was tedious and boring and i want no surpises on december.

    BTW, all of the passed the test. Just in case i`m planning to load them only with the 60% capacity.
     
  5. fasteddy

    fasteddy I have C.L.A.P Global Moderator Generous Elf

    Joined:
    Apr 26, 2010
    Messages:
    6,471
    Likes Received:
    16
    Location:
    Albion Park NSW
    Find Me On:
    You should test these on an individual basis on a seperate circuit first. Check to make sure that the voltage setting switch is set to 230v instead of 115v. If they work then add an extra power supply to the circuit and continue doing this until you have your total load. If they all work on an individual basis but not as a group then it can be caused by either in rush current or earth leakage. So try seperating the power supplies onto different circuits.

    I personally use meanwells now days
     
  6. OP
    OP
    dpavisic

    dpavisic Full Time Elf

    Joined:
    May 12, 2010
    Messages:
    211
    Likes Received:
    0
    Location:
    Sydney
    [/quote]
    I am sure you meant 350 watt not 350 volt... right?
    Actually, look at the specs, they have one hell of an inrush current. They may not be defective at all.
    [/quote]

    Yes I meant 350 Watts. Sorry.

    I was plugging them in separately without any load but they kept blowing the fuse. Whats an inrush current?

    In any case these 2 are at the tip and I am using some mean wells that I found which I must have ordered some time ago. I will be getting more mean wells for next year.

    Thanks for the responses.
     
  7. David_AVD

    David_AVD Good news, everyone!

    Joined:
    Jun 12, 2010
    Messages:
    3,345
    Likes Received:
    22
    Location:
    Victoria Point (Brisbane)
    The "inrush current" is the initial surge drawn (from the mains) when power is first applied to a switch-mode power supply. It can be up to 40 Amps per power supply, but only for a very brief duration.

    Fuses and circuit breakers don't respond instantaneously, so that's why your 15A or 20A fuse/breaker doesn't blow/trip even with the (brief) 40A surge.

    If a single power supply is tripping a 20A breaker, I'd say it's more than likely faulty.
     