Tune to P5 Pannel blowing fuses

Croydon Lights

Full time elf
Generous elf
Joined
Jan 6, 2018
Messages
200
I need some help with my Tune to P5 panel that keeps on blowing fuses after a couple of hours running
The pannel is made up off 3 x 4 outdoor P5 panels with a 7.5 amp fuses providing power to each two panels
There is no vent for heat to escape or circulation, could this be cause of the problem ?
 
The current for 2 P5 panels is potentially over the 7.5A rating of the fuses depending on the panel brightness. If there is a gradual buildup of heat then the fuse trip current will decrease. For a 30 degree temperature rise there will be a drop in the capacity of about 5%. If you're running at higher than the rated current of the fuse then the trip curve also comes into play.
I'd drop a fuse out and put a multimeter across the fuse terminals on the current range and have a look at what current you are actually drawing while displaying stuff.

1767617694345.png1767617511547.png
 
Hi! Did you ever find out what was causing the fuses to blow?

I work with Azar Pixel, where we repair LED displays, and intermittent faults like this are worth checking under the same brightness and operating conditions where they occur. Along with the current draw already mentioned, it may help to inspect the panel power cables and connectors for damage or discoloration with the system powered off. Avoid fitting a larger fuse until the cause and the wiring’s ratings have been checked.

I’d be interested to hear what you found—it could help someone else with a similar P5 setup.
 