Honest question right? If voltage drop in the 5V compared to a 12V pixel string is due to the 20AWG wire, why not just ask for 18AWG wire to be used? I could see there being a challenge with soldering the larger wire down to the pad on the circuit board, but...

I already emailed Ray, but does anybody have any thoughts on the matter?

I went to an online calculator and punched in 20AWG wire, DC, 5V, 1.4A string current (what I have measured on my 50 count bullet style ws2811 strings running with white light) with a string length of around 9 meters... The calculator suggests that the voltage drop should be 0.8V so from 5.0V to 4.2V.... which would be great, but I'm seeing closer to 1.8V drop to 3.2V at pixel 50...

If I fiddle with the wire gauge setting in the calculator, I see that the the voltage drop I'm getting would make more sense for a 23AWG wire... and I believe I have ready around here that someone had counted strands and measured diameters to find that the 20AWG was not really 20AWG...

So, let's just say that the 20AWG used in the wire is really 23AWG... and we get a 1.8V drop... which requires power injection every 50 pixels for 5V applications... why not just bump up the gauge wire... I'm showing that a 16AWG wire should allow for 100 pixels of 5V with acceptable voltage drop (to 3.4V at pixel 100).

Thoughts?

-Louie
 

AAH

I love blinky lights :)
Community project designer
Joined
Dec 27, 2010
Messages
4,188
Location
Eaglehawk
The Chinese understanding of specifications might be the problem.
CE for most of the world is a quality standard that stands for Conformité Européenne . With budget priced stuff that comes from China I'm sure it just stands for Chinese Export.

AWG is generally assumed to stand for American Wire Gauge. The Chinese equivalent is Any Wire Gauge

:) :) :) :)
 

nutz4lights

Full time elf
Joined
Dec 12, 2012
Messages
305
Location
Melbourne, Florida
I understand all of that, but he sells 20AWG and 18AWG hook-up wire (should I say "20AWG" and "18AWG" ??) in his store... and appears to use "20AWG" in the light strings... even shifting to 18AWG.... sorry "18AWG" would be an improvement... and the cost difference between those two gauges seems minimal.

-Louie
 

ChristmasInKaralee

Senior elf
Joined
Feb 15, 2014
Messages
620
Location
Karalee
nutz4lights said:
I understand all of that, but he sells 20AWG and 18AWG hook-up wire (should I say "20AWG" and "18AWG" ??) in his store... and appears to use "20AWG" in the light strings... even shifting to 18AWG.... sorry "18AWG" would be an improvement... and the cost difference between those two gauges seems minimal.

-Louie

Yes at least with Rays stuff the 18awg is bigger then the 20awg. They may not be equal to the CE AWG but at least the lower number is a thicker wire.

Ray can have anything made so if there is something on the site that is 20 AWG then I'm sure he can make it 18awg.
 

fasteddy

I have C.L.A.P
Global moderator
Joined
Apr 26, 2010
Messages
6,648
Location
Albion Park NSW
I think one of the issue may be that these are primarily designed around sign lighting which don't suffer from voltage drop issues due to the local nature of power supplies. The other thing that may be an issue is the moulding and the PCB and if they can adequately accept and use a thicker gauge, if they cant then this requires new moulds and investment for new tooling which may make this idea unfeasible in the eyes of the manufacturer. But no harm in trying to see if Ray would give it a go
 

scamper

Dedicated elf
Joined
Jan 5, 2014
Messages
1,225
Location
collie
The other factor that you need to consider is the drop across the pcb and components themselves, As you say the voltage drop is larger than it calculates it should be, I would hazard a guess that that is from the board and not the wire.
 

nutz4lights

Full time elf
Joined
Dec 12, 2012
Messages
305
Location
Melbourne, Florida
scamper said:
The other factor that you need to consider is the drop across the pcb and components themselves, As you say the voltage drop is larger than it calculates it should be, I would hazard a guess that that is from the board and not the wire.
That could be confirmed with a non sealed string, which Ray and others on eBay do sell... off to ebay I go... good suggestion. I work in circuit board design and fabrication, so I may have to tear one of these down to look at copper weights, layer count, trace width, via size, etc...

Louie
 

MichaelF5

Apprentice elf
Joined
Nov 23, 2016
Messages
76
Location
West Hoxton
Has anyone figured out if Ray's happy to look at other sizes of cable on custom jobs... or any other vendors by that matter? anyone also find if the pixels themselves cause much of a voltage drop other than their usage? I assume the main power basically goes straight through each pixel..
 

ezellner

Full time elf
Joined
Feb 12, 2017
Messages
126
Location
West Bloomfield, Michigan, USA
I have ordered 18 AWG pixels from Ray and the gauge is definitely larger than what comes standard. I use 5 V pixels throughout and these have worked very well for me without any noticeable voltage drop for my runs.
 

brando

Full time elf
Joined
Nov 26, 2021
Messages
130
Location
Ormeau, Qld
I just asked Ray if I could order a couple thousand 5V with bigger wire, he said max is 18AWG.

I did a quick test over 3 strings on tester. 5.16V at connection to tester, 4.6 end of first string, 3.7 end of second, 3.15 end of third
 

brando

Full time elf
Joined
Nov 26, 2021
Messages
130
Location
Ormeau, Qld
Some other reading - https://auschristmaslighting.com/threads/pixel-wires-the-downright-ugly-truth.14335/

@brando better to ask if you can get that 18awg wire in copper

Really need to clean up some of these really old threads
I just chimed in because I had to send him a message anyway and figured I’d ask. I went 5V the expectation of having to inject from string 3 and every two after. Though I'm guessing this thread was originally posted in a time when Ray's pixels came with 20AWG? All before my time. I have to pay attention to post dates on recycled threads.
 
Last edited:

MichaelF5

Apprentice elf
Joined
Nov 23, 2016
Messages
76
Location
West Hoxton
Sorry, could not find anything newer, feel free to auto lock anything over 2 years.. I just hunt for the most appropriate as most of the posters are still around!
 
Top